Hi Team,
As you can see below I am not getting SKU value, can you please let me know how fix it? Even when extracting the report I am getting the date instead of the Serial number.
There is a OID for the model number, from which you could look up the associated battery type. And before now I have not seen any entry in their MIB Structure for battery type/sku.
This is only because I have never looked so far down the line.
I found Internal and External SKU
upsIdentModel 1.3.6.1.2.1.33.1.1.2
Specifically for APC Smart UPS : 1.3.6.1.4.1.318.1.1.1.1.1.1.0 System Model
-CharlesH
Loop1 Systems: SolarWinds Training and Professional Services
Hi CharlesH,
Thank you for the giving the answers. Actually,Ii have set-up a dashboard as UNDP for ups. Do we need to create one more UNDP for below:
Specifically for APC Smart-UPS : 1.3.6.1.4.1.318.1.1.1.1.1.1.0 System Model
thanks.
If you want the device model # then setup one of those OID's as another UnDP - test both to see which works best across your range of models.
If you are not getting anything returned on the SKU OID's (1.3.6.1.4.1.318.1.1.1.2.2.19, & 20) try using GetNext. (or Get with a .0 at the end).
I tested this on what I had available (small smartups 450's) The 9606 and 9617 cards do not return anything. The 9630 returns all 0's. You may need a 9631, or it may be manually set like the battery replace date.
Hi Cahunt,
Thank you for the update.
Yes, I am using the same OID but no luck, getting the same error.