    kk74859

      Has anyone assigned a NPM poller to gather Temp, Humidity, Fan speed from a SRCOOL12K Air Conditioner \ SRCOOLNET (SNMP Network device)? I have added this device to NPM but can not figure how to gather Temp, etc..

       

      Any advice would be appreciated. I have not added custom pollers and would need instructions on how to do so. ! ! !

        • Re: SRCOOLNET Poller
          eriskit

          I know this has been floating in cyber space for a couple of years with no answer.

          I myself had the very same question and a trip to the Tripp-Lite web site wasn't all that helpful either.

          I was able to download the MIB's for the SRCOOLNET device and walk through it with the iReasoning MIB browser.

          Loaded up the MIBS and bounced some queries against the SRCOOLNET. I was able to confirm the following OID's...

          The following link was sent to me on how to create custom UNDP pollers.

          https://support.solarwinds.com/Success_Center/Network_Performance_Monitor_(NPM)/Knowledgebase_Articles/Create_a_Universal_Device_Poller_UnDP_-_Video

           

          Below you will see the description of the OID, and a sample of the responses I have harvested from my machine. I have included a few comments.

          Sorry about the formatting...

           

          Ident info group .1.3.6.1.4.1.850.104.1.1

           

          Model Info

          OID: .1.3.6.1.4.1.850.104.1.1.1.0

          Value: SR(X)COOL12K

          Type: OctetString

           

          Manufacturer

          OID: .1.3.6.1.4.1.850.104.1.1.2.0

          Value: TrippLite

          Type: OctetString

           

          Serial #

          OID: .1.3.6.1.4.1.850.104.1.1.3.0

          Value: #################

          Type: OctetString

           

          Software Version

          OID: .1.3.6.1.4.1.850.104.1.1.4.0

          Value: 12.06.0069.13078.12917

          Type: OctetString

           

          Device Name

          OID: .1.3.6.1.4.1.850.104.1.1.5.0

          Value: AirConditioner2

          Type: OctetString

           

          Location information

          OID: .1.3.6.1.4.1.850.104.1.1.6.0

          Value: Datacenter rear corner

          Type: OctetString

           

          Current Mode

          OID: .1.3.6.1.4.1.850.104.1.2.1.0

          Value: cooling  (2)

          Type: Integer

           

          Fan Speed

          OID: .1.3.6.1.4.1.850.104.1.2.2.0

          Value: hi  (3)

          Type: Integer

           

          Return Air temp (no decimal point)

          OID: .1.3.6.1.4.1.850.104.1.2.3.0

          Value: 690

          Type: Integer

           

          Water level

          OID: .1.3.6.1.4.1.850.104.1.2.4.0

          Value: waterNotFull (0)

          Type: Integer

           

          Current Remote Temp (No decimal)

          OID: .1.3.6.1.4.1.850.104.1.2.5.0

          Value: 815

          Type: Integer

           

          Display units

          OID: .1.3.6.1.4.1.850.104.1.2.6.0

          Value: english (1)

          Type: Integer

           

          On/Off

          OID: .1.3.6.1.4.1.850.104.1.3.1.0

          Value: turnOnUnit  (1)

          Type: Integer

           

          Set Mode

          OID: .1.3.6.1.4.1.850.104.1.3.2.0

          Value: cooling (0)

          Type: Integer

           

          Set Point Temp (No decimal)

          OID: .1.3.6.1.4.1.850.104.1.3.3.0

          Value: 630

          Type: Integer

           

          Fan speed setting

          OID: .1.3.6.1.4.1.850.104.1.3.5.0

          Value: high (3)

          Type: Integer

           

          Remote Set Point enable

          OID: .1.3.6.1.4.1.850.104.1.3.6.0

          Value: disable (0)

          Type: Integer

           

          Fan Always on

          OID: .1.3.6.1.4.1.850.104.1.3.7.0

          Value: disable (0)

          Type: Integer