How to configure an advanced alert trigger condition to notify me when upsSecondsOnBattery is NOT equal to 0?

I am trying to set up an advanced alert to notify me when upsSecondsOnBattery is NOT equal to 0.  I have set up a UnDP for upsSecondsOnBattery.  Is the following correct?

upsSecondsOnBattery.PNG

  • Are you trying to determine if a UPS is actively using the battery?  What you have looks correct, though I'm not sure that I have used that particular MIB.  Here is what I have.  Note I have a few different vendors of UPS equipment.  Also I have a custom property that tells me if it is a critical UPS or just some small ups that I don't need an alert on.  Hope this helps.

    Capture.JPG

  • Yes, I assume that the UPS has lost input power if the upsSecondsOnBattery is greater than 0.  I would have preferred to be able to pick the value of the UnDP but that was as close as I could guess.

  • What brand of UPS do you have?  My ups systems support a undp that states the input source.  For APC, you'll want to browse for a mib called upsBasicOutputStatus (1.3.6.1.4.1.318.1.1.1.4.1.1).  A value of 1 is unknown. A value of 2 is Online and a value of 3 is battery.  I usually map the values and then use Value.  It's a little more friendly and it's treated as a string.  Tripplite has a similar mib, but I don't know the oid of the top of my head.